Lightning & Tool Trips

Fab tools trip in storms: surge or sag?

When tools trip during a thunderstorm, it's usually not because lightning struck the plant directly, but because lightning hit a transmission line and caused a voltage sag on the grid. Lightning arresters and surge protectors guard against overvoltage; they can't stop voltage sags. This article explains what actually happens during a thunderstorm, how to tell which problem you have, and what equipment fits each.

A nighttime thunderstorm with lightning striking a distant transmission tower, a lit semiconductor park in the foreground
Lightning hits a transmission line outside the plant; it doesn't need to hit the factory to affect the whole park (illustration)

Summary: storm trips

The most common reason fab tools trip during thunderstorms is a voltage sag: lightning strikes a transmission line and causes a short-circuit fault, pulling down voltage across the nearby grid for about 0.1 s, and the tools' control systems reset. Lightning arresters and surge protective devices (SPDs) only stop overvoltage surges, not voltage sags. To prevent these trips, add voltage sag compensators (sag protectors) or an online UPS to the control circuits that reset, and adjust protection settings such as undervoltage relays. Surge protectors keep equipment from being damaged by surges; you need both.

What happens in a storm?

Lightning affects factory power in two completely different ways:

  • Lightning reaches plant wiring→Surge: spike that can fry gear
  • Lightning hits an outside line→Sag: grid dips ~0.1 s
A substation on a stormy night, lightning striking distant high-voltage lines
Lightning hits the grid: the line shorts and protection isolates the fault; for about 0.1 s, voltage drops for every nearby customer (illustration)

The second is far more common than the first. Lightning doesn't need to hit your plant. If it hits a line on the same supply network and causes a short-circuit fault, protection equipment isolates the fault within a very short time, and every nearby customer experiences a voltage sag during that interval. Taipower also lists lightning as one of the main causes of voltage sags (Taipower FAQ: "What is a voltage sag?").

Surge vs. sag

Side by side: on the left, a circuit board scorched and smoking from a surge; on the right, a semiconductor tool with a black control screen and a warning light on, but no damage
Left: a surge burns out components. Right: a voltage sag stops the tool and blanks the screen; a restart usually fixes it (illustration)
Two power problems caused by lightning (compiled by DEYly)
ItemSurgeVoltage sag
Voltage changeSpikes above normalDrops to 10–90%
DurationMicroseconds~0.1 s typical
Typical resultFried boardsTrips; restart fixes it
Area affectedNear the strikeThe whole grid area
FixArresters, SPDsVoltage sag compensators, online UPS

Which one is it?

Rows of tools along a cleanroom aisle, all warning lights turned yellow at once, a technician in a cleanroom suit standing in the aisle
A whole row of tools lighting up and stopping at once is the classic sign of a voltage sag (illustration)
  1. Anything broken?

    Burned-out components or boards point to a surge; a tool that trips but runs normally after restart points to a voltage sag.

  2. Did the lights flicker?

    If the lights flickered or dimmed at the moment of the trip, voltage dropped across the whole site, a classic sign of a voltage sag.

  3. Same model tripping?

    If only certain models trip during the same storm, their control components are especially sensitive to sags.

  4. Do the times match other records?

    Cross-check equipment alarms, UPS input event logs, facility power monitoring, and lightning data from the weather service. If the times match, you can confirm a lightning-induced sag.

What prevents storm trips?

Factory electrical room: an open switchboard with breakers and surge protection modules, next to a white voltage sag compensator cabinet and a black online UPS cabinet
Surge protectors in the switchboard prevent burnout; the compensator and UPS cabinets beside it keep tools running through sags (illustration)
Equipment and measures that prevent thunderstorm trips
MeasureProblem it solvesProtectsNotes
Voltage sag compensator (sag protector)Voltage sagPLCs, IPCs, robots, control power, EMO circuitsControls only, small size; holds seconds
Online UPSSags and outagesMust-run loads3–6% loss; batteries every 3–5 yrs
Tune settingsVoltage sagUndervoltage relays, VFDsCheapest; ask the maker
Arresters, SPDsSurgesPanels, electronicsStops burnout, not sag trips

The most common misconception is "We already installed lightning arresters, so why do tools still trip in storms?" The two solve different problems: surge protectors keep equipment from being damaged; sag compensators keep equipment from stopping. In areas with frequent thunderstorms, you usually need both. For sizing a sag compensator, see "How to size it"; for the full set of prevention methods, see "How to prevent voltage sag trips in a factory."

4 things to do before storm season

A facility engineer in a hard hat measuring a switchboard with a handheld power quality analyzer on a stormy day, the screen showing a voltage sag waveform
Set up monitoring before thunderstorm season so the depth and duration of every sag are recorded (illustration)
  1. Compile last season's trip records

    Which days, which tools, how long each recovery took: start with a list.

  2. Find the worst models and parts

    Use alarm types to find whether the control power supply, contactor, or VFD drops out first.

  3. Fix the worst one first

    Adjust settings or add a compensator to the control circuit; thunderstorm season is the best time to verify.

  4. Set up monitoring

    Event logs from a power quality analyzer or the compensator itself record the time, depth, and waveform of every sag, so you can prove the improvement worked.

FAQ

We have lightning arresters and surge protectors. Why do tools still trip during thunderstorms?

Because lightning arresters and surge protectors stop overvoltage surges, while thunderstorm trips are mostly voltage sags: lightning hits a transmission line outside the plant, causing a short circuit that pulls grid voltage down for about 0.1 s. Preventing these trips requires a voltage sag compensator or an online UPS.

Lightning didn't hit the factory. Why do tools still trip?

Because if lightning hits a transmission line on the same supply network and causes a short-circuit fault, every nearby customer experiences a voltage sag. The factory doesn't need to be hit directly to be affected.

How do you prove a thunderstorm trip was a voltage sag?

Match the trip time against light flicker, UPS input event logs, facility power monitoring, and lightning data from the weather service. Matching times, equipment that runs normally after restart, and no burned components are the classic signs of a voltage sag. You can also ask your local Taipower district office whether there was a supply incident at the time.

What's the most effective equipment against thunderstorm trips in a fab?

Adding voltage sag compensators to the control circuits that reset is the most direct fix: they run in bypass normally and draw almost no power, and during a sag they switch in about 1 ms and hold for several seconds. Use an online UPS only for loads that must also survive outages.

Measure first

In your plant, which tools are most vulnerable to sags?

Book a voltage sag risk assessment. We use trip records and on-site measurements to find the equipment that really needs protection, then decide how to protect it.